Power for home lab/office

Handruin

Administrator
Joined
Jan 13, 2002
Messages
13,914
Location
USA
I'm sure how to tell if these batteries are past their useful life. I took the pack out and all four batteries were cool to the touch so I don't think my UPS continuously cooks them or runs warm. None of them were bulging or leaking anything and the pack was easy to slide out. I can pull the plug from the wall for a couple minutes and it runs a 600W load.

I measured the voltages on the cells and they read 13.4V on each cell or 26.9V on each pair. Should I still replace them?

1688408171881.png
 

LunarMist

I can't believe I'm a Fixture
Joined
Feb 1, 2003
Messages
17,450
Location
USA
It's a a question of how old they are. I have a special battery thingamajig, but you can put a constant load on them and test capacity manually. Your UPS is a 1500VA model?
 

Handruin

Administrator
Joined
Jan 13, 2002
Messages
13,914
Location
USA
Yes it's 1500VA model and the batteries are from January 2017 (6.5 years).
 

LunarMist

I can't believe I'm a Fixture
Joined
Feb 1, 2003
Messages
17,450
Location
USA
They will die soon enough and you don't want it to happen at a bad time when your NAS and computer experience an uncontrolled shutoff like mine. :(
 

Handruin

Administrator
Joined
Jan 13, 2002
Messages
13,914
Location
USA
That's fair. I went ahead and ordered the 12v 8AH Duracell you mentioned and got the 18% off.
 

Handruin

Administrator
Joined
Jan 13, 2002
Messages
13,914
Location
USA
Batteries got swapped and it was was easy enough to replace the 4-pack. I'll let it charge overnight and see how the voltages are.
 

LunarMist

I can't believe I'm a Fixture
Joined
Feb 1, 2003
Messages
17,450
Location
USA
All the AGM batteries are designed to float around 13.5-13.8V at room temperature. The 6 small UPS I've recently tested are all between 13.52-13.67V per battery. A large one is 27.1V and the other one cycles around 26.9-27.2V. There may be some hysteresis with the panel meter, but a graph shows spikes. I suppose that is normal since it's been that way for many years.
 

LunarMist

I can't believe I'm a Fixture
Joined
Feb 1, 2003
Messages
17,450
Location
USA
I wonder what JTR thinks about most UPS charging batteries from bulk to float without an absorption stage like a typical charger? How many hours are needed at 13.5-13.6V to reach 100%?
 

Handruin

Administrator
Joined
Jan 13, 2002
Messages
13,914
Location
USA
I just checked again with my voltage meter and 13.5V (27v for the pair) after charging so it's consistent with what you mentioned. I don't have any insight into the UPS charging mechanism.
 

ddrueding

Fixture
Joined
Feb 4, 2002
Messages
19,719
Location
Horsens, Denmark
I suspect it is due to the expected use cases. Sitting fully charged 99% of the time, with the occasional significant discharge spaced apart by months. It would be better if it wasn't, but likely a cost cutting measure.
 

LunarMist

I can't believe I'm a Fixture
Joined
Feb 1, 2003
Messages
17,450
Location
USA
It's possible that the float is enough because the battery is always on charge and not set aside. If the last 15-20% takes several hours or one hour may not make a practical difference.
 

LunarMist

I can't believe I'm a Fixture
Joined
Feb 1, 2003
Messages
17,450
Location
USA
My test results of the two 12V-9Ah FR are not so great. I'm not seeing much more capacity than the 8Ah and not a lot less impedance either. I'll put them in an olden APC 1300VA UPS for an AV center but it's not worth the one-third extra cost over 8Ah IMO. In my 24V 1500VA UPS with six (2 int/4 ext) batteries the FR (high rate) are definitely not needed since the drain on each is 1/3 of the 2-battery types.
Anyways, I am done with batteries for now (about $400 worth in a month or so).
 
Top